What kind of electrical service will this amp require?
80 amps. Typ 100 amps is used. A 100 amp breaker eats up 4 x slots in the 200 amp main panel.
On SSB / CW, 60/70 amps will work just fine, and only eats up 2 x slots. We used a 60 amp 2 pole breaker on buddy's YC-156 80-10 amplifier.... fed with 6 ga wire, but the HV supply is only 3' from his main 200 amp panel... but that YC-156 amp only does 7-8 kw pep out. Bottom line is, you require 200 amp service coming into the home.
If measuring the current, be careful. Only a true RMS AC current clamp on device will work. Or an Iron vane style panel meter with correct external XXX- 5 amp xfmr. Reason is, on any C input B+ supply, current is drawn in pulses...every 8.3 msecs. NON rms current metering wants to see a true 60 hz sinewave...not pulses every 8.3 msecs...(with each pulse lasting just 2-3 msecs).
Non rms metering will result in readings that are 20-40% lower than reality. I have a 0-300 amp, clamp on...that plugs into my small Fluke 87 DVM (true rms meter). DVM is switched to read vac. 300 amps = 3.0 vac on the DVM. 100 amps = 1.00 vac on the dvm. 50 amps = .50 vac. 10 amps = .1 vac. The fluke 87 is a true rms dvm...and that's for both ACV..and also AC current.
On ssb, you won't flicker any lights. The biggest issue with these bigger amplifiers is the V drop from the street. On buddy's 3x6 amp, with 12 kw out, key down, he loses 6 vac from the street..and another 2 vac (main 200 amp panel to HV supply, which is 20' away)..and fed with 2 ga wire). Basically we are dealing with un regulated B+ supplies. This is why taps are used on the pri of the plate xfmr. If your incoming line V measures 240 vac, the 235/230 tap is used. If your incoming line V is 250, use the 240 tap. My Dahl is tapped at 198-208-218-230-240-250. If I had to do it again, I would have gotten it tapped at 220-225-230-235-240-245.
Your real no load B+ is what the HV meter reads..when sucking normal idle current. You have to draw idle current 1st... before drive can be applied. I could care less what the B+ is on RX.